Can other equipment be installed within the fire dike of liquid ammonia spherical tanks?

2016-03-09View Original

Thread Content

Can equipment such as ammonia evaporators, ammonia off-gas absorption tanks, ammonia gas-liquid separators, and gaseous ammonia buffer tanks be installed within the fire dike of the 2 liquid ammonia spherical tanks (at normal temperature and medium pressure)?
Reply #22016-03-09
No, those devices should be placed separately in an area outside the ball tank fire dike
Reply #32016-03-10
Our leader came up with his own layout plan, placing all these devices inside the fire dike, and said that the client had approved it as well; he asked me to prepare the construction drawings. I just felt it wasn’t appropriate, though I couldn’t identify exactly which regulation prohibited it. Are there any specific requirements outlined in those regulations?
Reply #42016-03-31
Finally, a basis was found: DL/T5480-2013 \"Technical Specifications for the Design of Flue Gas Denitration in Thermal Power Plants\", page 22, 4.1.10: Full-pressure liquid ammonia storage tanks should be located within a fire dike, while other equipment related to these tanks should be placed outside the fire dike.
Reply #52016-04-03
Not to mention other equipment, according to the regulations of 2014, dikes must now also be installed between the two liquid ammonia sphere tanks.
Reply #62016-04-03
It was all for nothing – the management insisted that these auxiliary equipment be placed inside fire dikes, claiming that this is necessary in an explosion-proof area. The owner also started arguing, saying that in other liquid ammonia plants, the auxiliary equipment is indeed placed inside fire dikes. I was so angry; they didn’t even appreciate my efforts to consider their interests. Is it possible that the \"Technical Specifications for Flue Gas Denitration in Thermal Power Plants\" don’t apply to chemical plants? Are there any specific provisions in the petrochemical regulations, building codes, or other documents issued by the safety supervision authorities that forbid placing such auxiliary equipment inside fire dikes?
Reply #72016-04-04
50160 5.3.6 Requirements also apply to connected pumps. You should have higher demands for this one. I’ve highlighted it; let’s discuss it together.
Reply #82016-04-06
It doesn’t seem appropriate to place it inside the fire dike.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.