Seeking assistance with centralized monitoring system for instruments in chemical processing workshops

2016-03-23View Original

Thread Content

Now the factory plans to consolidate all the instruments on site onto a central control computer for real-time display and monitoring; it is intended solely for monitoring purposes, without the need for feedback control. Currently, the main instruments include pressure gauges, flow meters, level gauges, and thermometers. Some of these instruments display readings directly on a dial, while others are connected to digital displays for showing the readings. The factory currently does not have a central control computer. What work needs to be done if all the data displayed on the instruments is to be gathered and shown on one computer? What is the general process? Is a PLC or DCS control system needed, or some other approach? What software is generally used on the central control computer? Can the data on the digital display be sent directly to a computer, or output to a DCS or PLC?
Reply #22016-03-23
Just replace them all with electric instruments and add a PLC; you can’t possibly bring pneumatic instruments from the field into the control room
Reply #32016-03-23
Entering the control room requires electrical signal transmission; there needs to be a PLC cabinet (containing I/O cards), a host computer, as well as configuration software and monitoring software
Reply #42016-03-23
1. Replace all mechanical instruments in your workshop with transmitters. 2. Count the total number of AI points in your workshop. 3. Contact the intermediary specializing in automatic control systems (our factory uses a DCS system for centralized control), and tell them the number of points you have counted. 4. If there are many control points, it is recommended to use DCS; if there are few, use PLC
Reply #52016-03-23
Displaying the information is quite simple: it can be done via a computer display or through touch screen control. The pointer-type instruments need to be replaced with those that have an output signal function. As for the display itself, it’s necessary to determine whether it has communication capabilities; if not, a communication module needs to be added or the instrument replaced. A simpler approach is to find a company that can come to your site and carry out such an integrated control solution, replacing all the components that need to be changed at once. There are quite a few people who do this; if you need, I can also recommend some to you.
Reply #62016-03-23
There are so many software programs these days, and cracked versions sometimes lack complete functionality
Reply #72016-03-23
First, the signal is converted into a 4–20mA standard signal, which is then connected to the computer via a signal acquisition card; configuration software can be used, which makes the process simpler.
Reply #82016-03-24
Friend, could you please help recommend a few companies so I can inquire about them? Thank you.
Reply #92016-03-24
First, count the number of points; if there are 1000 points or more, go straight for a DCS system. Those that use quadratic displays can be connected directly to the DCS cabinet. On-site pressure gauges (without remote transmission functionality) and bimetallic thermometers cannot be integrated into the system. Among domestic DCS systems, HaliTech and Zhejiang University Control Systems are widely used; their prices are relatively low, and they are easy to configure and use. I have been using them since 2008 without any problems. For future projects such as new constructions or renovations, I buy some modules myself and configure them on my own, which is more cost-effective.
Reply #102016-03-24
We can create such monitoring systems; it’s very simple for us. We have controlled many more complex devices than this, some of which are controlled via touch screens and others through computer software. Consult at qq378673499
Reply #112016-03-24
First of all, it is necessary to replace the locally displayed instruments with remote-type ones, that is, those equipped with transmitters. If the number of IO points is low, a domestic PLC can be used as it is cheaper; one operator station will suffice. As for the software and configuration packages, they can be given to the PLC manufacturer.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.