FF bus instrument enthusiasts, come and exchange ideas!

2016-03-24View Original

Thread Content

When the instrument shows PV-BAD and can recover after power is cut off (some instruments show OOS from time to time), what are the common causes? Things that cannot be restored – generally, after replacing the instruments, they can be commissioned. What aspects need attention during routine maintenance? Aside from shielding and grounding, I hope experts can offer more guidance
Reply #22016-03-25
It’s probably a problem with the instrument’s status. The FF instrument has two states: one is the OOS state you mentioned, and the other is AUTO. When the instrument is working properly, it should be in the AUTO state; otherwise, it doesn’t produce any output. Go to the site and check the header display to see if the status is correct There’s not much to do for routine maintenance; a 475 model that supports the FF protocol is required.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.