Calibration issues with Rosemount 3051 pressure gauges

2016-03-31View Original

Thread Content

Help: Which option on the handheld controller can be used to calibrate a 12mA current? If the range is -100 to 100 KPa, how do I calibrate 0 KPa? ? Can the output current be customized?
Reply #22016-03-31
It seems that the handheld controller cannot be calibrated for 12mA; in such cases, I usually set it to 0–100 KPa, calibrate it at 4mA, and then adjust it back to the desired range. There are buttons on the gauge, and it is also possible to adjust the zero point; since it is a gauge pressure meter, it can be zeroed out. The hand controller can define the transmitter’s output current, and is generally used for backflow verification.
Reply #32016-03-31
Rosemount doesn’t have such a concept as calibrated current; it is generally calibrated at zero
Reply #42016-03-31
Apply pressure, bring the pressure to 0. 475 can force the instrument to output current in the absence of a pressure source.
Reply #52016-03-31
After I disassembled the gauge, its reading is off by a few KPa – how do I calibrate it? What does forced output current v mean?
Reply #62016-03-31
This should be a gauge for absolute pressure; do not calibrate it casually – to zero it, negative pressure must be applied
Reply #72016-03-31
What exactly do you want to do? Do you really have to set it to 0? Take it off; the range is from -100 to 100. Then, after taking it off, does it display the pressure in kPa? In that case, do not disassemble it. At the installation location, change the range to 0 to 100, and then check whether the instrument displays 0. If not, use the 475 device to perform the Zero Trim function; after that, it will display 0, and you can then change the range back to its original value. Forced output, circuit testing – some people call it setting a value; it involves making the instrument output X milliamps and then checking whether the system receives the same value.
Reply #82016-03-31
Find a standard calibrator, set the pressure to zero, and then use Hart to perform zero trim
Reply #92016-04-01
Mm-hmm, I know. I just wanted to ask if it’s possible to set the handheld controller to 0 without changing its range
Reply #102016-04-02
For such gauges, when setting the zero point, we usually first adjust the range to 0 to 200, then calibrate the zero point, and afterward change it to -100 to 100. After adjusting the range, there is a deviation of around 0.00 several!
Reply #112016-04-02
Can EJA’s gauge be calibrated to 12mA?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.