Distance between the foam connector of the oil spill tank and the cofferdam

2016-04-03View Original

Thread Content

Our oil tank has a capacity of 200 cubic meters, and we want to add fire protection vertical pipes. What is the distance required between the quick connectors and the cofferdam, or rather, from the tank wall? Please provide clear guidelines, thank you
Reply #22016-04-04
Those who understand up there, please explain it to them; if you don’t understand, then stop talking nonsense. Do you realize what your level is?
Reply #32016-04-05
The poster is referring to semi-fixed foam fire extinguishers; the quick connectors should be placed outside the cofferdam for easy use, as placing them inside the cofferdam makes it difficult to operate in case of an accident.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.