Hello, teacher: For the Zhejiang University Zhongkong DCS system, how should one configure it on the computer after installing new level transmitters at the site?
It depends on the requirements shown; sometimes it’s in terms of specific meters, and other times it’s in percentages. In any case, the range for the level transmitter is set in meters
In the hardware configuration section, it’s convenient to set information such as signal type and engineering units for each IO template channel.
In simple terms: 1. Add a tag point to the tag table, and set the channel address and range. 2. If there are no specific logic control requirements for that level transmitter, then it’s simple – just add a tag point in the flowchart and reference that point. 3. If PID control is required, then a PID function block needs to be configured; after that, all that’s left is to download and deploy it
It mainly depends on what system you are using. Zhejiang University’s control systems now include several different types, so it varies from case to case!
The answer for floor 4 is basically correct, but it’s indeed necessary to know your system model. Select the card address and add a point, set the attribute information (tag number, annotation, range, alarm, etc.), and configure this point on the monitoring screen. After adding a new point, remember to update the point table. Different configurations require different methods of operation, but the general approach is similar.