1. For the remote pressure transmitter of the liquid ammonia storage tank (design pressure: 2.5 MPa, diameter: 3 meters), what type of process interface should be used – flange type or 1/2 NPT? It would be good to also mention the relevant instruments and valves;
Reply #22016-04-21
The measurement pipeline doesn’t need to be cooled, right? Ammonia is toxic, irritating, and corrosive; it’s better to use flange connections. Using Hastelloy for the transmitter diaphragm is no problem. For the primary valve, a needle valve or gate valve will suffice, while a 316 stainless steel ball valve will work well for the secondary valve. Let’s see how the experts recover
Reply #32016-04-21
This post was last edited by budaoweng123 on 2016-4-21 at 20:57. A flanged connection is necessary; there are straight sections of pipe and ball valves between the pressure transmitter and the tank here.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.