Why does a refrigerator have high exhaust pressure and high oil pressure when the load is very low?

2016-04-30View Original

Thread Content

The propylene twin-screw refrigeration machine in our unit exhibits high exhaust pressure and high oil pressure under light load conditions. Specific parameters: Suction pressure: 158 kPa (absolute pressure), Suction temperature: -15 degrees Celsius. Exhaust pressure: 1638 kPa, exhaust temperature: 66 degrees Celsius. Oil pressure: 1914 kPa, oil temperature: 44 degrees Celsius. Load: 7%. The cooling water system is operating normally. What’s the reason for that, please?
Reply #22016-05-01
Correction: The twin-screw refrigerators using ethylene (not propylene) in our facility experience high exhaust pressure and high oil pressure when the load is very low. Specific parameters: Suction pressure: 158 kPa (absolute pressure), Suction temperature: -15 degrees Celsius. Exhaust pressure: 1638 kPa, exhaust temperature: 66 degrees Celsius. Oil pressure: 1914 kPa, oil temperature: 44 degrees Celsius. Load: 7%. The cooling water system is functioning properly, and the refrigerant is ammonia. What’s the reason for that, please?
Reply #32016-05-01
The oil drain pipe is positioned too high, preventing the oil inside from being completely drained
Reply #42016-05-01
Could you explain in detail whether it could be due to the oil separator?
Reply #52016-05-06
The pipeline from the evaporator to the salt water tank – the oil drain port is located there. Is the oil drainage position too high, in my opinion?
Reply #62016-05-07
Thank you very much. The reason has been identified: the two twin-screw refrigeration units share one evaporator, with one unit being used for processing while the other maintains production operations. During the processing, that unit was not isolated with a blind flange, resulting in nitrogen entering the refrigeration machine that was maintaining production operations. In other words, the non-condensable gas causes high pressure.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.