What are the operation steps for adjusting the float level gauge reading of HART475 according to the glass plate indication?

2016-05-20View Original

Thread Content

The float level gauge is not giving accurate readings now; the process team believes that the glass plate level gauge is accurate, and they want the readings to be adjusted according to those of the glass plate. What are the operating steps for 475?
Reply #22016-05-20
The range and density should be set properly, and then verification should be carried out (using water for calibration or the medium to be measured). If the verification is successful, there should be no problems. The installation positions of the buoy and the glass plate are generally not the same, so their relative relationship needs to be determined.
Reply #32016-05-21
What you said is all correct. Modify the numbers directly, use logarithms, based on the glass plate.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.