What are the fire separation distances required between torches and walls, roads, civil buildings, Class A and B factories or storage areas, as well as tank areas? ? Which provision states that? Thank you!
It is mentioned in both building fire protection codes and petrochemical fire protection codes. The former is more geared towards factories and warehouses, while the latter focuses on installations; it depends on which one you decide to implement If you think it’s reasonable, please vote for the best assistance :)
Could you list which article it is? Thank you!
Building codes: 3.4.1, 3.4.3, 3.5.1, 3.5.2, 4.2.1, 4.2.9, 4.3.1; Petrochemical codes: 5.2.1, 4.2.12. It is advisable to consult the relevant codes in detail.
Sir, I took a look – none of these regulations mention the fire separation distances required between torches and walls, roads, as well as civilian buildings, right? ? ? ?
This requires looking not only at the text of the provisions but also at the explanations accompanying them; some are provided in those explanations
Sir, could you please specify which provision mentions it? I’ve searched for ages but couldn’t find it; I’m really troubling you here!
Article 4.1.9 of the Petrochemical Regulations specifies requirements regarding elevated flares in relation to walls, roadsides, buildings, as well as the explanatory notes accompanying the provisions