Seeking advice on issues with double-acting valve positioners

2016-06-15View Original

Thread Content

For a double-acting positioner, the air circuit has one input and two outputs. I would like to know whether air is supplied to both outputs at any valve position, or only to one of them
Reply #22016-06-15
Theoretically, as long as it’s not in the fully open or fully closed position, both circuits will have air pressure. This is necessary to maintain stable valve position.
Reply #32016-06-15
As long as it is not in the fully open or fully closed position, both circuits have air pressure. This is necessary to maintain stable valve position.
Reply #42016-06-15
This can be set to single-acting
Reply #52016-06-16
Both paths have output; when both are turned on or both are turned off, it can be considered that the other path also has output, but the output value is 0

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.