How are the wires connected to the ammeter on the field operation column?

2016-07-13View Original

Thread Content

Current transformers are installed on the low-voltage switchgear circuits in the distribution room, along with a digital current meter. Now, a pointer-type ammeter needs to be installed on the motor’s local control panel. So, how should the wires of this ammeter be connected on the side of the low-voltage switchgear?
Reply #22016-07-13
Just connect the current signals in series....
Reply #32016-07-13
The ammeter is connected on the side of the low-voltage switchgear, via terminal blocks!
Reply #42016-07-14
When connected in series, does choosing a secondary current of 1A or 5A for the current transformer have any impact on the operation panel? What should I be careful about?
Reply #52016-07-14
When connected in series, does choosing a secondary current of 1A or 5A for the current transformer have any impact on the operation panel? What should I be careful about?
Reply #62016-07-18
Just combine the two tables, right?
Reply #72016-07-19
Parallel connection isn’t possible; the voltage transformer is used for measuring current in the main circuit, and the current in the main circuit equals the sum of the currents in the branch circuits. It can only be connected in series.
Reply #82016-07-19
Then, the ammeter at the site must be connected using copper-wired cables that are run to a location away from the site; as a result, these wires will have resistance, and therefore the current reading will definitely be lower than that of the ammeter installed in the switchgear. And the readings shown are all around half of the circuit current; this error is way too large. Don’t deceive me – I’ve also studied physics in junior high school.
Reply #92016-07-21
It means that the ammeter on the control column should have the same transformation ratio as that of the current transformer, right?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.