HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

How to calibrate pressure values with a pressure transmitter

2016-07-22View Original

Thread Content

The last edit to this post was made by dboy82 on 2016-7-22 at 08:52. Taking a Rosemount 3051 with a range of 0 to 6 MPa as an example, I used a handheld controller to calibrate the PV value, but this only corrected the current output: before calibration, the standard pressure was 0 MPa, PV was 0 MPa, and AO was 4 mA; Calibration pressure: 6 MPa, PV: 6.18, AO: 20.5 mA; no change at the 0 point after calibration ; Full-scale calibration point: (standard pressure source of 6 MPa) The instrument displays PV as 6.18 MPa, and the AO output is 20 mA. Thus, after calibration the output of this pressure transducer is normal, but the pressure value shown on the transducer’s gauge is still incorrect. May I ask if it is possible to adjust the PV value of the voltage transformer? How to adjust?
Reply #22016-07-22
Does the handheld controller have a heavy-duty range option?
Reply #32016-07-22
There is an option to reset the range, which is also set from 0 to 6 MPa
Reply #42016-07-22
Your question is the exact opposite of this friend’s question! It should output the module number; it shows a module failure. You can take a look at this post: [Request for help] The display on the field gauge of the pressure transmitter differs from that in the control room
Reply #52016-07-22
What do you want to do, change the upper range limit? Or do you apply 6 pressure, and the gauge reads 6.18? Which function of the 475 are you using?
Reply #62016-07-23
The PV value can’t be changed, right? Only the zero point and range can be adjusted. It’s possible that the diaphragm is deformed. However, some boards have a potentiometer, and it is recommended not to touch it.
Reply #72016-07-23
This post was last edited by ssln123 on 2016-7-23 at 11:01. How is the standard pressure determined – using a piston-type pressure gauge or a digital hand pump? If the standard table is qualified, it means that your voltage transformer is broken.
Reply #82016-07-25
The PV value cannot be changed; it can only be altered by adjusting the range, which in turn affects the output

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.