Participation reward: 2 Wealth. Reward for the correct answer: 9 Wealth. Which of the following statements is correct? ( )   A. In power circuits with a directly grounded neutral point that are used specifically at construction sites, a TN-C neutral protection system must be employed. B. The bases of insulators, the flanges of bushings, protective nets (covers), and busbar supports, as well as other accessible exposed conductors, must be reliably grounded (PE) or connected to the neutral (PEN). It shall not be used as a connecting conductor for grounding (PR) or bonding to neutral (PEN). C. When a regular copper wire is used as the protective conductor, its cross-sectional area shall be no less than 2.5 mm² when mechanical protection is provided; it shall be no less than 5 mm² when no mechanical protection is available. D. Metal cable supports and cable conduits must be reliably grounded (PE) or bonded to neutral (PEN). Correct answers: BD
Reply #22016-08-26
The correct statements are (BD).   A. In power circuits with a directly grounded neutral point that are used specifically at construction sites, a TN-C neutral protection system must be employed. B. The bases of insulators, the flanges of bushings, protective nets (covers), and busbar supports, as well as other accessible exposed conductors, must be reliably grounded (PE) or connected to the neutral (PEN). It shall not be used as a connecting conductor for grounding (PR) or neutral connection (PEN). C. When a conventional copper wire is used as the protective conductor, its cross-sectional area shall be no less than 2.5 mm² when mechanical protection is provided; it shall be no less than 5 mm² when no mechanical protection is available. D. Metal cable supports and cable conduits must be reliably grounded (PE) or connected to the neutral (PEN)
Reply #32016-08-26
B. The bases of insulators, the flanges of bushings, protective nets (covers), and busbar supports, as well as other accessible exposed conductors, should be reliably grounded (PE) or connected to the neutral (PEN). It shall not be used as a connecting conductor for grounding (PR) or neutral connection (PEN). D. Metal cable supports and cable conduits must be reliably grounded (PE) or connected to the neutral (PEN)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.