Participation reward: 2 Wealth. Reward for correct answer: 9 Wealth. Which of the following statements is incorrect? ( )   A. When angle steel is used as an artificial grounding electrode and is laid underground, its minimum thickness is 4 mm. B. For grounding wires buried in the ground, without any anti-corrosion protection but with mechanical protection, the minimum cross-sectional area of the copper conductor is 25 mm². C. For the distribution circuits of hand-held and mobile electrical equipment, residual current protection is advisable, with a tripping current of 30 mA. D. For the distribution circuits of electrical equipment at construction sites, residual current protection is advisable, with a tripping current of 20–50 mA. Correct answers: CD
Reply #22016-09-03
The incorrect statement is (CD).   A. When angle steel is used as an artificial grounding electrode buried underground, its minimum thickness is 4 mm. B. For grounding wires buried in the ground, without any anti-corrosion protection but with mechanical protection, the minimum cross-sectional area of the copper conductor is 25 mm². C. For the power distribution circuits of hand-held and mobile electrical equipment, residual current protection is advisable, with a tripping current of 30 mA. D. For the power distribution circuits of electrical equipment at construction sites, residual current protection is advisable, with a tripping current of 20–50 mA
Reply #32016-09-03
The incorrect statement is (CD).   A. When angle steel is used as an artificial grounding electrode buried underground, its minimum thickness is 4 mm. B. For grounding wires buried in the ground, without any anti-corrosion protection but with mechanical protection, the minimum cross-sectional area of the copper conductor is 25 mm². C. For the power distribution circuits of hand-held and mobile electrical equipment, residual current protection is advisable, with a tripping current of 30 mA. D. For the power distribution circuits of electrical equipment at construction sites, residual current protection is advisable, with a tripping current of 20–50 mA
Reply #42016-09-03
D. For the power distribution circuits of electrical equipment at construction sites, residual current protection should be installed, with a tripping current of 20–50 mA
Reply #52016-09-03
The incorrect statement is (CD).   A. When angle steel is used as an artificial grounding electrode buried underground, its minimum thickness is 4 mm. B. For grounding wires buried in the ground, without any anti-corrosion protection but with mechanical protection, the minimum cross-sectional area of the copper conductor should be 25 mm². C. For the distribution circuits of hand-held and mobile electrical equipment, residual current protection is advisable, with a tripping current of 30 mA. D. For the distribution circuits of electrical equipment at construction sites, residual current protection is advisable, with a tripping current of 20–50 mA
Reply #62016-09-03
CD、、、、、、、、、
Reply #72016-09-03
The incorrect statement is (c).

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.