I would like to know the differences between ASCO551 and 531 solenoid valves

2016-09-30View Original

Thread Content

I would like to know the difference between the ASCO 551 and 531 solenoid valves. In our company, the wiring for the solenoid valves is as follows: DCS card – relay – 551 solenoid valve; DCS card – safety barrier – relay – 531 solenoid valve (the 551 cannot be used in place of the 531). Could you please explain why the 551 cannot replace the 531 solenoid valve?
Reply #22016-09-30
This post was last edited by ssln123 on 2016-9-30 at 17:22. I’ve really never seen a DCS card–safety barrier–relay setup with two layers of isolation like this; the requirements are quite high.
Reply #32016-09-30
The 551 series monostable slide valves come with IEC 61508 functional safety data certified by TUV, allowing for a safety level of up to SIL 4/AK 7; the 531 series does not have such certification. Thus, from a security perspective, the areas of use differ, even though the functions implemented can be the same.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.