Why can a 10KV transformer installed in Workshop Class A supply power only to that workshop and not to the adjacent workshop?

2016-10-10View Original

Thread Content

Why can a 10KV transformer installed in Workshop Class A supply power only to that workshop and not to the adjacent workshop? Which standard requires this? I can’t find it.
Reply #22016-10-14
Take a look at 50016, fire protection codes :)
Reply #32016-12-10
According to the Code for Fire Protection Design of Buildings, Article 3.3.14 (mandatory provision), substation rooms shall not be located within or adjacent to Class A and Class B factories, nor in areas prone to explosive gases or dust. Substation rooms rated at 10 KV or below and intended for use exclusively in Class A and Class B factories may be built adjacent to such factories provided that they are separated by a fire wall without any doors or openings. It shall also comply with the relevant provisions of GB50058.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.