2016-10-25View Original

Thread Content

May I ask how to use a multimeter to calibrate the zero point of a differential pressure transmitter?
Reply #22016-10-26
The zero-point output current can be measured at 4 mA, but the accuracy and number of digits of the meter must be 1/3 of those of the differential pressure transmitter.
Reply #32016-10-26
For users, it is generally sufficient to adjust the range; the zero setting has already been done before manufacturing.
Reply #42016-10-26
A multimeter can be used for a simple assessment, but verification is not possible as the accuracy of a multimeter is not sufficient. One can only read zero; simply connect the milliampere range of the multimeter in series with the output terminal of the transmitter.
Reply #52016-10-26
This post was last edited by Wang Tianze on 2016-10-30 at 18:55. In other words, it’s like having a wrench, **********. If you are studying instrumentation, it is recommended that you go through the textbooks again.
Reply #62016-10-30
For a regular differential pressure gauge, simply close the high and low pressure sides of the three-valve assembly and open the balance valve; if the reading is 0 and the measurement current is 4 mA, then everything is normal:lol
Reply #72016-11-03
This post was last edited by cqdfwy on 2016-11-3 at 11:52. Generally, once the range is set, it can be used for a long time (unless the transmitter has poor performance or high usage requirements), but the zero point may drift over time; therefore, it needs to be checked regularly, and adjustments may sometimes be necessary.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.