Can the new electromagnetic flowmeter, which is 3 cm longer than the original one, be installed? ? ? The newly purchased gauge is 3 cm longer than the old one (the new gauge has a higher pressure rating, which is why its length is 3 cm greater; the new gauge is 33.124 cm long, while the old one is 30 cm long). It features flange mounting, flat welding, a convex surface, and is made of carbon steel
Absolutely not; it’s 3 cm long – where can I find any extra length?
Is it possible to grind off the flanges on the pipe, 1 cm on each side?
In this case, a section of the pipe is usually removed. When installing the flow meter, it should not cause stress on the pipeline; therefore, it should not be forced in.
Since the pressure rating of the flange has changed, the flange that matches the flow meter should also be replaced. When replacing the original pipe flange, it’s sufficient to remove just a small amount of the pipe that was welded to the flange. Do you want to use the old flange as before? It turns out that those flanges couldn’t be connected either to the new flanges of the flow meter.
In the end, it was decided to replace the pipe; fortunately it wasn’t too long, so a new section was made
I’ve checked the information; although the pressure rating has changed, the parameters of the flange remain the same. In the end, it was decided to replace the pipe; fortunately it wasn’t too long, so a new section was made