Problems with Honeywell pressure transmitters.

2016-12-07View Original

Thread Content

I have a pressure transmitter here, with a range of -0.1 to 0.6 Mpa; I’m filling the tank with 0. The 2mpa pressure gauge reads 0. 4 MPa; it’s the same whether it’s positive or negative pressure, and the measured pressure value is doubled – this is the figure shown by the pressure transmitter on site. Please, expert, help me figure this out!
Reply #22016-12-07
How about trying a float-type pressure gauge with a standard source?
Reply #32016-12-07
I tried it with a piston press yesterday, and the reading also doubled
Reply #42016-12-07
It also doubled; that’s due to drifting. Re-calibrate zero and span
Reply #52016-12-07
Calibrate the pressure transmitter first by yourself
Reply #62016-12-07
What device is used to measure 0.2MPa? If it is a standard gauge that is used for measurement, then the transmitter is faulty; calibrate the transmitter using a standard gauge.
Reply #72016-12-07
-0.05Mpa displays -0.1Mpa
Reply #82016-12-08
Why do pressure instruments have positive and negative pressures?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.