The voltage reads 10V when the 24V TOPWORX proximity switch is not in the closed state, which causes the PLC to think it is in the closed position – what is the problem?

2016-12-12View Original

Thread Content

As the title suggests, I need experts to help solve this problem; waiting online
Reply #22016-12-12
Then you need to check the technical specifications of this proximity switch – what is the voltage at which the proximity switch gets triggered?
Reply #32016-12-12
During on-site debugging, everything else is normal; 0V is available, but 24V is not. There’s only one problem; I don’t know where to start to fix it
Reply #42016-12-12
If we refer to other good proximity switches, it’s very likely that there is a problem with this one; try replacing it, or try installing a good proximity switch from the field on this device
Reply #52016-12-12
Is there a loose connection somewhere? Or there is a resistance in the circuit that causes voltage division
Reply #62016-12-13
Typically, the DI of a PLC can only be connected to mechanical switches, not proximity switches. So you need to install a DI safety barrier-type conversion module to convert the proximity switch signal into a mechanical switch signal
Reply #72016-12-15
Learned it, thanks for the discussion: handshake

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.