Differential pressure transmitter

2016-12-12View Original

Thread Content

Fault condition: The primary element is an orifice plate, and the differential pressure transmitter is the measuring instrument. When the system was put into operation, the output of the differential pressure transmitter did not rise but instead dropped below zero.
Reply #22016-12-12
Are the positive and negative terminals of the differential pressure transmitter connected in reverse?
Reply #32016-12-12
First, ensure that the transmitter is accurate and the wiring is correct; The three-valve block switch is correct. If the three-valve assembly is placed in a shutdown mode and the transmitter is reset to zero, it can be preliminarily determined that there is no issue with the transmitter; instead, it is the pipeline that is blocked ; Conversely, it could be a problem with the transmitter.
Reply #42016-12-12
The transmitter is fine; it has been tested.
Reply #52016-12-12
Common simple faults. . . Positive pressure condition Transmitter condition
Reply #62016-12-12
In this case, it’s best to use a handheld controller to check what the PV value of the transmitter is
Reply #72016-12-12
Is it like this since it was just put into operation, or has it always been this way? What is the medium being measured? Pressure and temperature parameters must be provided in order to conduct the analysis.
Reply #82016-12-13
Put it on backwards? If not, then there is indeed a pressure difference, with higher pressure on the back side

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.