2016-12-28View Original

Thread Content

The methanol tank area requires additional isolation valves, as well as cables, instrument air, and other such items. Are there any regulations regarding the explosion-proof rating or safety requirements for these elements?
Reply #22016-12-28
Yes, according to the explosion protection regulations, Appendix C: methanol is classified as grade IIA with an ignition temperature of T2; therefore, the explosion-proof electrical equipment used must be of grade IAT2 or higher.
Reply #32016-12-28
For cut-off valves, it is possible to specify the explosion-proof rating required from the manufacturer; but how is the rating for cables and cable trays determined? The explosion-proof rating of such electrical components must be equal to or higher than IIAT2
Reply #42016-12-28
Refer to GB50058-2014 \"Code for Design of Electrical Installations in Explosive Atmospheres\" Section 5.4 Design of Electrical Circuits in Explosive Environments
Reply #52016-12-29
Thank you. I’ll first look for the specifications
Reply #62016-12-29
I don’t understand. If we use fiberglass cable trays, 2*1.5 shielded cables, and a voltage of 220 volts, will that meet the safety requirements?
Reply #72016-12-29
If the methanol tank is a floating roof tank, the explosive hazard area is Zone 2; If the methanol tank is a dome tank and the explosive atmosphere is Zone 1, the cross-sectional area of the cable wiring shall be determined according to Table 5.4.1-1.
Reply #82016-12-29
What is a cable used for? The instrument wires can be run through galvanized pipes in the cable tray to the control room.
Reply #92016-12-30
The top is fixed; a fiberglass cable tray is used inside, and 2*1.5 shielded cables are employed to handle 220V voltage

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.