Chemical Process Equipment Area: [Weekly Topic] Vacuum issues with the turbine reheat Apparatus? (2011.6.20~6.26)
Thread Content
I invite everyone to start discussing vacuum levels in the new week. Turbines have high requirements regarding vacuum levels; what are the impacts of good or poor vacuum conditions on the unit? It is best to illustrate with actual examples. I hope everyone will participate actively. Special note: Those who post excellently will receive a reward of 10 to 50 Wealth points or an equivalent amount of Charm.3.2.1 Strengthen the recording and analysis of the temperature difference at the heater ends. When an increase in this temperature difference is detected, it should be analyzed and addressed promptly. If there are non-condensable gases such as air inside the heater, the air vent valve of the heater can be opened wider until the temperature difference returns to normal. If the heat transfer tubes of the heater are dirty, they can be cleaned while the heater is isolated from service. 3.2.2 Strengthen the monitoring of the heater’s operating condition, and make use of downtime to conduct inspections whenever possible. High-pressure heaters have high parameters and large heat capacity; if the steam extraction pipeline is equipped only with pneumatic check valves and electric isolation valves, they cannot be closed tightly and reliably. During unit operation, the isolation time for high-pressure heaters is long, so it is advisable to install manual isolation valves on the steam extraction pipeline to reduce maintenance time. 3.2.3 Increase the automatic activation rate of heater water levels to ensure that heaters operate with adequate water levels. Where feasible, replace some pneumatically operated control valves that cannot be automated with electrically operated control valves or jet regulators. 3.2.4 Regularly record the parameters of the heater and extraction steam. Since the lift of the stem of each extraction steam pneumatic check valve varies, the maximum stem lift for each check valve should be recorded for reference during analysis. 3.2.5 Strengthen the comparison of feedwater temperatures on the turbine and boiler sides; the electric valve of the high-pressure heater’s main bypass, which is currently controlled by intermission control to be closed in place, should be switched to torque control, and it is necessary to ensure that the inlet interlock valve is closed properly. 4 Unit vacuum 4.1 Impact of unit vacuum on economic efficiency The proper operation of the vacuum system has a significant impact on the economic efficiency of steam turbine operation. On the one hand, as the vacuum level decreases, the effective enthalpy drop of the steam is reduced; consequently, the generator output drops when the steam flow rate remains constant. When the generator output stays unchanged, the steam flow rate through the unit increases, resulting in a decline in the unit’s efficiency ; On the other hand, as the vacuum in the unit decreases and the temperature of the exhaust cylinder rises, the loss of cooling capacity in the unit increases, resulting in a decrease in the cycle thermal efficiency. Under normal circumstances, a 1% change in vacuum level can cause a 0.7–1% change in the heat rate, and a change of about 1 g/kW·h in coal consumption. 4.2 How to Improve Unit Vacuum 4.2.1 Conduct vacuum tightness tests in accordance with the regulations, carry out comprehensive analysis of operating parameters such as the water temperature at the inlet and outlet of the condenser, the terminal difference, vacuum level, and subcooling, identify the main factors affecting the unit’s vacuum, and formulate corresponding corrective measures. 4.2.2 Carefully carry out leak detection in the vacuum system using methods such as helium mass spectrometry and water flooding; promptly and thoroughly address any detected leaks. 4.2.3 Strengthen the maintenance and management of the condenser ball cleaning system to improve the cleaning efficiency. 4.2.4 Pay attention to adjusting the steam pressure of the shaft seal. On-site, in order to prevent the shaft seal steam from escaping, the pressure of the low-pressure shaft seal steam is often set quite low. Additionally, since the control valves in the overflow control system of the self-sealing system are pneumatic valves, their adjustments can result in significant fluctuations. All these factors contribute to leaks at the low-pressure shaft seal, and this is a fairly common problem. 4.2.5 Maintaining the water temperature in the spray tank at a low level: Tests on a 300MW unit have shown that when the operating water temperature varies within the range of 26–42°C, for every 1°C increase in water temperature, the vacuum decreases by approximately 0.065–0.133 kPa, which results in an increase in coal consumption of about 0.24 grams per kilowatt-hour. 5 Main and reheat steam parameters of the unit
5.1 Influence of main and reheat steam parameters on the unit’s economic efficiency
When the temperature and pressure of the main and reheat steam decrease, the effective enthalpy drop of the steam is reduced. With a constant steam flow rate, the generator output declines; conversely, when the generator output remains unchanged, the steam flow rate through the unit increases, thereby reducing its overall economic efficiency. Theoretically speaking: increasing the temperatures and pressures of the main and reheat steam in a power unit can improve its economic efficiency. However, higher temperatures also raise the temperatures of the equipment and pipes, accelerating the creep rate of the materials and reducing their creep limits ; The increase in main and reheat steam pressure raises the internal stresses on equipment and pipelines; it also increases the final moisture content of the steam, thereby exacerbating corrosion on the last-stage blades of the turbine and seriously jeopardizing the operational safety of the unit. Although the water injection for cooling in the boiler and reheaters is designed to be used as an auxiliary fine-tuning method or in emergency situations, due to advantages such as low inertia in response to water injection and a large temperature adjustment range, operators on site often use it as a regular tuning method, which has a significant impact on the thermal efficiency of the unit. In the case of spray desuperheating in superheaters, since most of the desuperheating water is taken from the outlet of the feed pump and the inlet of the high-pressure heater without passing through the high-pressure heater, it reduces the regenerative extraction steam and the degree of regeneration, thereby decreasing the thermal efficiency of the unit. In the case of reheat steam spray desuperheating, its thermodynamic process involves heat absorption and evaporation at constant pressure along the reheat pressure line, followed by superheating; thereafter, the steam enters the intermediate- and low-pressure cylinders of the turbine to expand and do work. The cycle it completes is a non-reheat cycle operating at medium or lower parameters. Compared to the main cycle (a high- or ultra-high-parameter reheat cycle), its thermal efficiency is significantly lower. 5.2 How to ensure that the main and reheat steam parameters of the unit remain at rated values 5.2.1 Ensuring that the unit operates at the specified steam parameter values under the fixed-sliding-fixed regime. 5.2.2 Ensure the normal operation of the regenerative heating system and maintain the feedwater temperature at normal levels. 5.2.3 Improve the efficiency of the unit’s flow path as much as possible, while ensuring the parameters of the main and reheat steam. 5.2.4 Boiler operators should make frequent adjustments to keep the parameters of main and reheat steam within the specified limits. 5 Flow path of the unit 6.1 Impact of the efficiency of the unit’s flow path on economic performance The efficiency of the flow path refers to the ratio of the actual enthalpy drop in each cylinder to the ideal isentropic enthalpy drop. Factors such as scaling or blockage in the flow path, as well as excessive gaps in the shaft seals and steam seals, can lead to a decrease in the efficiency of the unit’s flow path, which directly affects its thermal efficiency; in severe cases, it can also impact the unit’s output. Due to constraints in design and manufacturing at the time, the flow-through components of older units generally had low efficiency. For instance, the #9 and #10 steam turbines at the Xigu Power Plant in Lanzhou are 165 MW turbines of the ЛТ—140/165-130/15-2 type manufactured in Russia. Under rated operating conditions, the efficiency of their low-pressure cylinders was 75.28% and 77.31%, respectively. After adjustments to the steam seal clearances, replacement of the steam seals, and maintenance of the flow path, these efficiencies increased to 87.45% and 89.52%. Consequently, the heat rate of the units decreased by 587.42 kJ/kW·h and 543.21 kJ/kW·h, while the coal-free power output rose by 15.22 MW and 14.26 MW (all aforementioned indicators include the efficiency gains resulting from major overhauls). It is evident that the efficiency of the flow path has a significant impact on the thermal economy of the units. More and more power units are now equipped with DEH (electronic control systems), which enable valve management. Single-valve control is used during the initial stages of startup, and valve sequencing control is activated under certain conditions, thereby increasing the startup speed of the unit and ensuring higher economic efficiency. If single-valve control is still used during the normal operation of the unit, throttling losses will occur, affecting the unit’s thermal efficiency. In one unit, excessive vibration occurred due to valve control; therefore, single-valve control was used throughout its normal operation. Tests showed that the efficiency of the high-pressure cylinder was 3.48% and 3.77% lower at output levels of 300MW and 270MW, respectively, compared to units of the same type. 6.2 How to improve the efficiency of the flow-through components of the unit 6.2.1 During major overhauls of the unit, the flow-through components should be carefully inspected; any scaling or blockages should be addressed promptly. 6.2.2 After understanding the characteristics of the unit, the gaps such as those in the shaft seals and steam seals can be adjusted to the lower and middle limits specified by the manufacturer. 6.2.3 Older units can consider undergoing modifications to their flow-related components, provided that funding and schedule constraints permit it. Leakage conditions of Unit 7. 7.1 Impact of unit leakage on economic efficiency. Unit leakage can be categorized into two types: external leakage and internal leakage. External leakage of the unit refers to the leakage of steam and water from the thermal system due to imperfections in the pipes or systems. With the loss of these working fluids, there is a loss of energy associated with various flavors. Internal leakage refers to the situation where, due to improper sealing of valves, steam and water leak from a high-parameter section to a low-parameter section within a thermal system. Although no energy escapes the thermal system as in the case of external leakage, these working fluids only participate in the low-parameter thermal cycle, thereby reducing their ability to perform work and decreasing the thermal efficiency of the unit. 7.2 How to reduce unit leaks 7.2.1 Improve the quality of maintenance; use methods such as raising the pressure rating of valves to ensure they close tightly and prevent repeated leaks. 7.2.2 Due to the complexity of the steam turbine drain system and the large number of valves involved, as well as the difficulty in operating some valves, it is necessary to thoroughly check after each normal startup whether all valves are tightly closed. In particular, nowadays an increasing number of units employ SCS (Sequential Control); in such cases, electric valves are used to automatically control the opening and closing of drains. Since electric valves may not close tightly, extra care must be taken during inspection. 7.2.3 Strengthen the inspection and patrol of equipment systems. Use various methods such as touch, listening, and smelling to check for any system leaks; promptly and thoroughly address any leak points found. For issues that cannot be resolved during the unit’s operation, take measures to isolate them as much as possible. 8 Change the starting method of the feed water pump. For units with a capacity of over 300MW, a combination of steam-driven feed water pumps and electric feed water pumps is used. According to the manufacturer’s guidelines, during the initial stages of startup, the electric feed water pump is used to supply water; when the load reaches 100MW, the first steam-driven feed water pump is started, and when the load reaches 150MW, the second feed water pump is started, while the electric feed water pump is switched off and put on standby. This mode of operation has the following two drawbacks: During the cold start of Unit 8.1, it takes a long time to go from starting the electric feedwater pump to reaching a load of 100 MW (that is, starting the steam feedwater pump), and this process consumes a large amount of plant electricity. 8.2 When a steam-driven pump is started, it takes some time to warm up; if the pump needs to be warmed up further, even more time is required. Therefore, before the turbine-driven feed water pump of the unit is started, if a fault occurs in the electric feed water pump, the turbine-driven feed water pump cannot be put into service immediately. This may result in an interruption of boiler feed water supply, thereby causing the entire unit to fail to start. Therefore, the startup method can be improved: at the initial stage of unit startup, the electric feed pump is not activated; instead, the pre-pump of the steam-driven feed pump is used to supply water to the boiler in place of the electric feed pump. Before the pressure in the boiler drum rises to the point where the feed pump can no longer draw in water, the steam-driven feed pump is started directly (with steam supplied by the plant’s own new steam as well as steam from adjacent units). The opportunity provided by using the small steam turbine to increase its speed and warm up the system is taken advantage of to further raise the feed water pressure in order to meet the boiler’s water supply requirements. When a certain load is reached, the steam source for the small turbine is switched, that is, the steam supply is changed from fresh steam or steam from an adjacent unit to the fourth-stage extraction steam of this turbine. This method of starting has the following advantages: 8.2.1 During the initial stage of unit startup, water is supplied by electric feedwater pumps. Since the efficiency of the hydraulic coupling is much lower at low loads compared to that of a small steam turbine, and there are also mechanical and electrical losses as well as losses in power transmission, a significant amount of energy is lost ; In the improved starting method, since the efficiency of the small steam turbine changes little with load variations and it drives the feed water pump directly, there are few intermediate energy conversion steps, resulting in good thermal efficiency. 8.2.2 In the traditional startup method, when it is necessary to start the steam-driven feed water pump at a load of 100 MW, warm-up of the turbine and pump must be carried out (if required). This inevitably consumes a portion of the fourth-stage extraction steam, resulting in a waste of thermal energy. 8.2.3 If the small steam turbine is started using the main steam of the unit itself, the live steam is discharged to the condenser via a bypass. Therefore, the steam utilized by the small steam turbine can be regarded as “waste steam” being put to use. This helps increase the boiler’s evaporation rate, facilitates boiler combustion, and accelerates the rate at which the system heats up and pressure rises. 4. Throughout the startup process, the electric feed water pump remains in a standby state, and due to its fast startup speed, it enhances the reliability of unit startup. 9 Effects on boiler efficiency: There are many factors that affect boiler efficiency, mainly including the oxygen level in the boiler, flue gas temperature, fly ash, the air leakage rate of the boiler, the type of coal used, and the cleanliness of the boiler’s heating surfaces. How to improve boiler efficiency 9.1 Ensure an appropriate excess air coefficient for the boiler, with oxygen levels controlled at 4.0±0.5% (adjust as appropriate depending on the type of coal used). 9.2 The flue gas temperature is related to the cleanliness of the boiler’s heating surfaces and the boiler air leakage rate, as well as to the fineness of the pulverized coal. During normal operation, it is necessary to maintain an appropriate fineness and uniformity of the pulverized coal, while also adjusting the ratio between primary and secondary air. 9.3 In terms of boiler fly ash control, it should be carried out simultaneously with the adjustment of flue gas temperature; regular testing of fly ash and slag is necessary to obtain first-hand data for adjusting boiler combustion. 10 Summary: There are many factors that affect the thermal efficiency of power units; above, a brief analysis has been provided on a few of the main factors. The thermal economy of the unit is not only related to the operators and maintenance personnel specializing in turbines, but also closely associated with other professionals involved in the unit as well as its operating mode. Only through collaborative efforts, careful operation and maintenance, and meticulous servicing can the thermal economy of the unit be maximized. References: 1. Steam Turbine Operation Procedures for Plant 2 of Xigu Thermal Power Co., Ltd. 2. Centralized Control Operation Procedures for Plant 3 of Xigu Thermal Power Co., Ltd. 3. Zheng TiKuan • Thermal Power Plants • Water Resources and Electric Power Press