The safety valve has a front handwheel but no rear handwheel; for those safety valves whose outlet leads to a flare system, can they be taken offline for testing?

2022-05-23View Original

Thread Content

It is used with flammable and explosive media, and the safety valve has only a front hand valve, no back hand valve. It leads directly to the flare stack behind the valve – can this safety valve be taken out of service?
Reply #22022-05-23
Ask the person in charge of verification.:D
Reply #32022-05-23
The main goal is to take the safety valve offline for calibration. Let’s see if anyone has a better way.
Reply #42022-05-24
Close the upstream valve, remove the safety valve, and then plug the pipe leading to the flare with a blind flange
Reply #52022-05-25
No, it does not meet the requirements for safe maintenance. It can cause leaks of flammable gases or toxic gases!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.