Thread Content
When measuring liquid pressure, is the location of the pressure tapping point on the device located in the range of 0∽45 degrees below the horizontal centerline, just like in the pipeline?
Yes, the location of the pressure tapping point is within the range of 0 to 45 degrees below the horizontal centerline. .
Okay, thank you! I have another question for you: are there any requirements regarding the orientation of the temperature sensor? Are there any relevant specifications?
The installation location of the temperature sensor should be chosen such that it can represent the temperature of the medium, avoiding interference from external environmental factors or the device’s own heat sources. It is usually necessary to avoid locations with heat sources or direct sunlight, and consideration also needs to be given to the ease of equipment maintenance and sensor replacement. The specific orientation shall be determined based on the actual operating conditions and equipment status.
Can yarn, pipes, and equipment be the same? The pressure is set within the 45° range to ensure the accuracy of pressure measurement. Where is the 45-degree horizontal line on your device?
Equipment is different from pipes; according to the requirements for inspection, maintenance, and instrument installation, it is generally located on the side that facilitates operation, such as on the side of the passage, within a diameter range of 0.6 to 0.8 times that of the equipment’s pipe outlet