The power factor on the high-voltage side is different from that on the low-voltage side

2018-05-14View Original

Thread Content

The power factor on the high-voltage side is different from that on the low-voltage side: phase A on the high-voltage side shows a value of 0.45–0.75, while phase C shows 0.93. The overall power factor ends up being between 0.75 and 0.91. There is an automatic reactive power compensation device installed on the low-voltage side; the value of 0.85 shown there is it due to three-phase imbalance?
Reply #22018-05-14
Based on your question, it is powered by a transformer of 10/0.4kV or 6.3/0.4kV. The power factor on the high-voltage side is low because the reactive losses associated with the transformer have to be taken into account; therefore it is lower than that on the low-voltage side. Your high-voltage side certainly lacks reactive power compensation ; The three-phase imbalance in the power factor on the high-voltage side is caused by the three-phase imbalance in the power factor on the low-voltage side, which is reflected on the high-voltage side.
Reply #32018-05-16
Yes, it’s 10/0.4 KV; no reactive power compensation is installed on the high-voltage side – it’s mainly present on the low-voltage side. Since it’s a distribution transformer, it’s almost always either unloaded or lightly loaded. Where should we look to find the problem?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.