Burnout of current transformer in high-voltage motor

2020-06-04View Original

Thread Content

The motor of the reciprocating compressor has a voltage of 10,000 volts and a current of 160 A. After starting under no load, it stopped automatically after a short time; inspection revealed that the current transformer in the power distribution room was damaged. After inspection, the mechanical components of the compressor are in good condition, and the crankshaft rotation is normal. What could be the reasons for this to happen?
Reply #22020-06-22
1. A secondary open circuit generates a high voltage. 2. When a current transformer is in use for an excessive period of time, its insulation deteriorates, leading to local breakdowns or discharges that generate overvoltage. 3. The primary connection surface of the current transformer is severely oxidized, resulting in high contact resistance.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.