HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Discussion on the basic requirements for safety control in key chemical processes under stringent supervision

2022-08-10View Original

Thread Content

Dear everyone, regarding the basic requirements for safety control in chemically intensive processes that require close monitoring, should such interlocks be implemented within the DCS system for general control, or within the SIS system?
Reply #22022-08-10
Analyze it: those that need to be integrated into SIS should be done so, while those that don’t require it can be controlled via DCS
Reply #32022-08-11
This post was last edited by zhaisanming1 on 2022-8-11 at 09:27. The interlock control within the framework mentioned above is basic interlock control; if a DCS is required, it is similar to the mandatory requirements. For the SIS system, an HOZIP analysis must be conducted first before deciding whether supplementary measures equivalent to those of a DCS are needed. My personal understanding.
Reply #42022-08-11
I understand it the same way, but there’s no solid basis to rely on, so I’m a bit lost now
Reply #52022-08-12
The requirements mentioned above refer to the functions that the DCS system should possess. The first list of key processes was published in 2008, while the State Administration of Work Safety issued requirements regarding safety instrumented systems in Document No. 116 from 2014; the chronological order makes this clear
Reply #62022-08-12
Interlocking needs to be implemented in a DCS system with general control. It should be possible to tell by looking at the LOPA protection layer analysis.
Reply #72022-08-13
To conduct a LOPA analysis and determine the SIL level, choose between SIS and DCS based on that SIL level

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.