Distance requirements between Class C warehouses and initial rainwater ponds

2017-04-18View Original

Thread Content

The initial rainwater ponds are those for the nearby Class A and Class C facilities as well as the tank farm. May I ask: is there any requirement for a safety distance from Class C warehouses?
Reply #22017-04-18
There is no requirement in GB50160; however, for septic tanks and oil separation tanks, a distance of 20 meters needs to be considered
Reply #32017-04-19
If it is used merely as a rainwater tank and is classified as a Class D installation along with Class C warehouses in accordance with GB50160, the fire hazard increases once oil is present; in such cases, the fire hazard must be determined based on the properties of the substances contained

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.