When designing the cooling side of a heat exchanger, should water flow be controlled through the inlet water or the return water?

2019-08-22View Original

Thread Content

This post was last edited by yiyuguchen on 2019-8-22 at 14:52. When designing the cooling side of a heat exchanger, should a control valve be installed on the circulating cooling supply pipeline or on the circulating cooling return pipeline, in order to regulate the amount of circulating water based on the cooling temperature of the material?
Reply #22019-08-22
By adding control valves for the return water and feed water, can it be ensured that the heat exchanger is always filled with fluid? ? ? ? ? ? ? ? ? ? ? ? ? ? ? ?
Reply #32019-08-23
I personally recommend using it in the outlet pipeline... to ensure that the cooling water can fill the equipment. But... I’ve also seen designs that use it at the inlet end. I asked whether such an approach was reasonable, but all I got in response was that it’s just for cooling anyway. This type of setup is something that the production unit modifies on its own, with no logic at all behind it
Reply #42019-08-23
In all heat exchangers, the cooling medium flows in from below and out from above, which ensures that the cooling water fills the entire condenser or heat exchanger; usually, the inlet is installed, while the outlet remains open at all times. Of course, you can also install it on the outlet. It is merely installed on the outlet, so the heat exchanger is under pressure all the time.
Reply #52019-08-23
Experienced engineers install the control valves for circulating water at the outlet, with the aim of preventing the dissolved oxygen from being released as the temperature of the circulating water rises, which could otherwise accelerate equipment corrosion. There are fewer and fewer experts who are aware of this reason!
Reply #62019-08-26
For vertically installed heat exchangers, the inlet and outlet can be installed either way, as long as the tubes inside the heat exchanger are fully filled; for horizontally installed ones, the outlet should be placed at that end.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.