Is it feasible to replace the compensation wire with copper wire?

2017-02-23View Original

Thread Content

There is now a medium-pressure steam pipeline, with a balance flow meter; the transmitter is of the direct-mounted type and has pressure stabilization compensation functionality, capable of measuring differential pressure and pressure on its own. A K-type thermocouple is installed about one or two meters downstream of it to measure temperature. The signal from the thermocouple needs to be connected to a differential pressure transmitter; what impact will there be if no compensation wire is used in this case? Since both ends of the compensation wire are at roughly the same ambient temperature and the distance between them is short, can a central conductor be used as a substitute?
Reply #22017-02-23
It is best to use compensation wires, as there is still a difference between the temperature at the wiring box of the steam pipe thermocouple and the temperature at the transmitter. If copper wire is used, the error is the temperature difference between the two locations.
Reply #32017-02-23
Our company has thermocouples on two pumps, which are connected to the transmitter via terminal cables; the length of these cables is 6 meters. There have been no issues with its usage
Reply #42017-02-24
It’s 2m long – not in stock? Otherwise, it’s very troublesome to troubleshoot when problems arise.
Reply #52017-02-24
For steam temperature and pressure compensation, it is best to use compensation wires
Reply #62017-02-24
No, only Type B thermocouples can use copper wire as a compensation wire.
Reply #72017-02-24
If it is possible to keep the temperatures of the two equal in an open environment, it is difficult to achieve this with insulation; in such cases, a compensation wire should be used
Reply #82017-02-24
No problem. It’s equivalent to creating a two-meter-long terminal block.
Reply #92017-02-24
Sure enough, they are all masters:D Now I recall a question from before: \"The thermocouples in the DCS cabinets that were used in the past were connected to the safety barrier through compensation wires; then why was copper wire used for the connection from the safety barrier to the card device, given that the card device also needs to receive signals from the thermocouples?\" It’s because both the safety barrier and the card holder are inside the cabinet, so their temperatures are roughly the same; it’s best to have them in the same cabinet. Try to ensure that the temperature at the safety barrier terminals and at the clamping elements is similar
Reply #102017-02-24
As long as the temperature difference is not too large, it can be used
Reply #112017-02-24
Personally, I think it’s fine to use a thermal resistor without a compensation wire, as the temperature isn’t very high

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.