Cable issue

2017-03-26View Original

Thread Content

There is now a level switch that is four-wire type, operating on 24V power supply plus signal lines; can one 1*4*1.5 cable be used for this purpose, or are two 1*2*1.5 cables necessary? Are there any guidelines I can refer to?
Reply #22017-03-26
Different signals should not use the same cable.
Reply #32017-03-26
I think using a 4-core wire is fine, but I’ve never seen any specifications regarding it.
Reply #42017-03-26
They are all instrument signals, and the signal voltage is low; no problem
Reply #52017-03-26
At first glance at the question, I thought there were cable problems everywhere. If proper installation is possible, use 4 cores; if it’s not a hassle, use two pairs of 2 cores each
Reply #62017-03-27
For digital signals, 4*1.5 should be fine
Reply #72017-03-27
It is best to use a 2x(2x1.5) split-screen main cable, as this complies with the specifications for selecting instrument cables.
Reply #82017-03-27
When the power supply and digital signal circuits are in different cabinets within the cabinet room, it is advisable to use two separate two-core cables, as this makes it easier to arrange the cables within the cabinet room.
Reply #92017-03-27
It depends on whether the level switch you have provides 1 or 2 inlet ports

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.