2017-06-09View Original

Thread Content

Some 1.5 square millimeter single-core control cables have arrived at the site; using a multimeter, the resistance of each cable was found to be 27 ohms, and their length is 2200 meters. Are such control cables considered acceptable?
Reply #22017-06-10
Cable acceptance should not be based solely on the conductance resistance; tests such as voltage withstanding tests and insulation tests are equally important. You didn’t specify the exact model of the cable, so I can only provide a standard; you can use the instructions included there for inspection.
Reply #32017-06-10
Did Xi’an Metro fail because of the control cables?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.