[Weekly Accident Case Sharing] Accident Case 3: Misoperation of the valve position switch.

2017-08-22View Original

Thread Content

This post was last edited by tiandiyi*an on 2017-8-22 at 10:01. I. Fault symptoms: At 11:56 on May 20, 2016, the main steam valve interlock caused Unit #1 of a certain company to shut down, which in turn led to the shutdown of the #1 rich gas compressor. The instrumentation and control personnel inspected the position switch for the high-pressure main steam valve and found water accumulation in the switch corresponding to the fully closed position of the #1 high-pressure main steam valve. II. Cause analysis: (1) Water accumulation in the full-close position switch of the #1 high-pressure main steam valve, which is part of the shutdown logic, caused the full-close travel switch of the #1 high-pressure main steam valve to send false signals, and this condition persisted. When the #1 high-pressure main steam valve is fully closed, a turbine shutdown signal is generated, which triggers the protection mechanism of the #1 rich gas compressor. (2) The steam leaking from the stem of #1 main steam valve condenses into water, which then seeps along the cables into the position switch, causing abnormal activation of the signal for fully closing the high-pressure main steam valve. (3) The signals used for logical protection in the control system and those used for display are from different sources, which prevents effective monitoring. (4) None of the various regulations require that ‘protection signals must be displayed on the operator station’; only the ‘reliability’ regulation stipulates that various fault conditions must be displayed on the operator station for operational analysis purposes. (It’s too obvious, which is why no one pays attention to it.) III. Problems identified: (1) Inadequate inspection and maintenance of the main steam valve position switch. During unit startup, steam leaked from the stem of the main steam valve; the waterproofing measures for the position switch of the main steam valve were inadequate, which caused the condensed steam to seep into the position switch along the cables. (2) There are deficiencies in protection combing, resulting in the signals used by the control system for logical interlock protection and the signals displayed on the screens having different sources. IV. Preventive measures: (1) Display important interlock protection signals on the operator panel to ensure that these signals are consistent with those shown on the operator’s screen, thereby facilitating monitoring. (2) Before conducting important online tests, instrument technicians should first carry out signal checks and resolve any issues found promptly. (3) In the event of steam or water leakage, the instrumentation team should promptly take protective measures and check whether there is water accumulation or a decrease in insulation in the relevant equipment.
Reply #22017-08-22
The travel switch for full closure of the main steam valve sends out a false signal; this signal should be displayed on the operator station to indicate that the main steam valve is fully closed, and it should also be sent to the interlock protection system to trigger an emergency shutdown. Why is it necessary to ensure that the signal from the interlock protection system matches the signal displayed on the operator’s screen? I don’t quite understand; could you explain?
Reply #32017-08-22
The incorrect valve position feedback referenced by the operator station is what caused the discrepancy with the interlock signal display. Also, in this incident, an old system was used; interlocks were not implemented within the SIS but rather through the DCS.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.