2017-08-25View Original

Thread Content

I’m a beginner when it comes to instruments. In my factory, there is a loading system, and one of the vortex flowmeters has an on-site display; however, even when fluid is flowing through it at a significant rate, the instantaneous flow rate shows as zero. The total flow rate also doesn’t increase, and the wiring seems to be fine! 24V DC power supply also works fine; I’m asking the experts here to help identify the issue.
Reply #22017-08-25
If conditions permit, use an object to tap the pipe next to the flow meter, causing noticeable vibrations in the pipe, and check whether there is any change in the flow meter’s instantaneous flow rate.
Reply #32017-08-25
Is there a flow display on the vortex flowmeter gauge? First, check the vortex flowmeter’s LCD display; if it is present, then the issue lies with the secondary instrument. Does your vortex flowmeter provide a 4-20mA output or a pulse output? If not, it’s a problem with the flow meter. You need to first determine whether it’s a problem with the first part or a problem with the second part.
Reply #42017-08-25
It’s a pulse output; the display is normal, which means fluid is flowing through it, but the gauge doesn’t move
Reply #52017-08-25
After knocking, it was shaken for a while as well, and the instantaneous flow rate remained zero the whole time
Reply #62017-08-28
Ask the manufacturer whether what they send you is a gauge for gas pressure or a gauge for liquid pressure. It’s very likely that he set the sensor sensitivity too low, causing it to be below the flow rate of the medium in your pipeline. If the sensitivity is increased, it will then be unable to resist vibration interference.
Reply #72017-08-29
Your pulse output is a cumulative value; is the vortex street type integrated or separate? Is it that the meter of the vortex flowmeter does not show the instantaneous flow rate, or is it that the loading instrument does not display it?
Reply #82017-08-29
Small-signal clipping, linear or zeroing?
Reply #92017-08-29
Check whether the settings for the gas and liquid media being measured are correct, whether the small-signal cutoff is set too high, examine whether there are any issues with the vortex generator, and then check if there are any problems with the vortex detector

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.