Help: PID tuning for electric actuators

2017-09-02View Original

Thread Content

The actuator flow rate is used as the control condition, but the flow rate varies significantly, resulting in unstable PID regulation (as shown in the figure). By sending a pulse signal to the control valve manually, the instantaneous flow rate of the flow meter increased by four cubic meters of water; under normal conditions it would increase by only one cubic meter. Both the flow meter and the control valve have been replaced – what could be the reason for this? Is there something wrong with the settings of the flow meter?
Reply #22017-09-02
The trend chart in the lower right corner represents the flow meter with unstable PID control
Reply #32017-09-02
The PID parameters aren’t tuned well; adjust them gradually
Reply #42017-09-02
Oscillations are occurring; the proportional or integral action is too strong. Try reducing the proportionality or integration value gradually.
Reply #52017-09-03
It might be a problem with the flow characteristics of the valve; perhaps the selection wasn’t done properly during the design phase.
Reply #62017-09-03
First, ensure that when in manual mode, the opening is fixed and the flow rate remains relatively stable; if the flow rate fluctuates greatly, or there is a problem with the actuator’s travel range, automatic mode cannot be activated. Both sensitivity and integration time have a stronger effect the smaller they are; be careful when making adjustments. Integration provides lead control but results in significant lag; adding differentiation helps, as is the case with temperature.
Reply #72017-09-03
Everything you’ve adjusted is causing oscillation; fortunately it’s an oscillation of constant amplitude. Try reducing the value of P and observe what happens!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.