What causes fluctuations in the temperature gauge of the reactor?

2018-04-14View Original

Thread Content

In recent days, I’ve noticed that the thermometer on the reactor keeps fluctuating up and down. I checked the wiring and found no problems, and replacing the heat transfer oil didn’t help either. I really don’t know where the problem lies. There is toluene in the reactor, and the temperature is generally between 15 and 115. I need an expert’s advice on this.,
Reply #22018-04-14
"Is the thermometer fluctuating?\" "Is the thermometer fluctuating?\" "“The thermometer is fluctuating,” really? . . With the spring blossoms in bloom, let me guess: it’s probably \"spring has arrived, and they’re in heat, ready to fall in love, right?\" Install another one and give it to a friend to try out. .
Reply #32018-04-14
First, you need to look at the curve to see how it fluctuates; sharp rises and falls are usually due to issues such as wiring problems, temperature changes, safety barriers, or surges. If it rises or falls slowly, it is mostly a process issue. If the cause cannot be identified, the substitution method can be used; most thermometers come with a sleeve.
Reply #42018-04-15
The thermometer isn’t behaving properly this season; it keeps showing erratic readings. We need to keep a close eye on it
Reply #52018-04-15
The process has always been like this; it’s only recently that fluctuations have started to appear
Reply #62018-04-15
Isn’t there a local bimetallic thermometer on site? If not, the remote transmitter can be temporarily removed and a local one installed so that the process engineers can observe the fluctuations on-site. If the fluctuations remain severe, it is not due to the instrument; the process team needs to investigate its own causes
Reply #72018-04-17
Check the insulation of the wires, with respect to ground and the enclosure, etc. The description is too brief; it should include details such as the type of thermometer and the wiring configuration.
Reply #82018-04-17
Is there a problem with the pipeline connecting the safety barrier and the card holder? Check it

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.