Regarding transmitter spare parts

2019-12-26View Original

Thread Content

The installation is of large scale, with a large number of pressure and differential pressure transmitters, as well as various models. How should spare parts be considered in such a situation? There are also these transmitters; if they have the same model, they can actually be replaced even if their measurement ranges differ
Reply #22019-12-26
For normal operation, a measurement value between 1/3 and 2/3 should be sufficient; there are no special requirements regarding other pressure media or similar factors
Reply #32019-12-27
A large range can replace a small range, but a small range cannot replace a large range
Reply #42019-12-27
It is best to choose the same model and type to avoid errors
Reply #52019-12-29
First, one should consider whether the production environments are the same, such as having the same range, but also whether they are resistant to acids and alkalis. Moreover, when submitting spare parts, you need to consider the likelihood of those parts being used. For example, the pressure transducer in the circulating water pipeline can, if nothing goes wrong, last for over a decade. Do you decide whether to report the spare parts or not? ? Today’s voltage transformers are quite durable; they do not experience excessive pressure (above the designed range), mechanical damage, or damage to the diaphragm boxes caused by inadequate insulation in winter. Actually, there is no need to prepare spare parts. You also need to consider production requirements; for example, in the case of critical interlock instruments, it is necessary to resolve any issues as soon as possible. You can’t wait for the procurement department to buy it for you, right? For the rest, those with less stringent production requirements can function just fine without spare parts.
Reply #62019-12-30
Thank you for your reply; you have thought very comprehensively. I’ve learned a lot!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.