Our cabinets are located on an eight-meter-high platform, with the cable trays situated below that platform. The design team provided access holes underneath each cabinet, but unfortunately dust gets into the cabinets through those holes. We used foam to seal them off in the past, but the effect wasn’t very good. I’m seeking advice from experts: how should we deal with this situation in our cabinet rooms? There’s a layer of dust on the cabinet fixtures now; the environment here is really poor! ! ! ! ! !
Reply #22018-07-07
I’m pushing myself to do it:lol:lol:lol:lol:lol
Reply #32018-07-07
I encountered such a problem in previous projects; using flame-retardant foam material for sealing gave very good results; I assume you are in areas such as boiler rooms where there is a lot of dust. If the cabinet room is not large and the company has instrument air available, try implementing slightly positive pressure ventilation in that room to reduce dust infiltration ; If the conditions do not permit it, the cable entry points in the interlayer (leading to the cabinets) can be enclosed separately using fireproof materials, creating a buffer area before the cables enter the cabinets; this should help to reduce the amount of dust that gets inside the cabinets. Additionally, the interlayer should also be kept as sealed as possible to reduce external dust from entering it; this is for reference only.
Reply #42018-07-08
Since the reason is clear, it’s still just one word: blockage. The suggestions made upstairs are good; in particular, the mezzanine area needs to be sealed off first. I need to find a time to clean the dust from the DCS.
Reply #52018-07-08
We used explosion-proof putty for sealing, and the result was excellent.
Reply #62018-07-08
It is sufficient to maintain a positive pressure inside the cabinet, that is, by supplying compressed air that has been depressurized
Reply #72018-07-10
There is an inlet at the bottom of each cabinet, with cables hanging there like dead things
Reply #82018-07-10
Thank you. It’s the boiler area – it’s covered in dust. The space inside the cable compartments is too large; the design includes lots of windows, as well as several expansion joints
Reply #92018-07-10
Previously, special devices were used for inspection and dust removal
Reply #102018-07-12
The interior of the cabinet is generally sealed with fire-resistant boards and fire-resistant mortar
Reply #112018-07-12
Seal the entrance to the interlayer, seal the windows, and provide additional sealing at the cabinet entrances to maintain a positive pressure inside the cabinet room

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.