Issues with the liquid level indicator of the hydrochloric acid storage tank

2018-07-29View Original

Thread Content

I work the night shift; I add hydrochloric acid to adjust the acidity. The level gauge of the hydrochloric acid storage tank shows intervals in the middle. I feel this is not normal. What caused it? How to adjust? Take a look at the picture specifically!
Reply #22018-07-29
If the magnetic flap isn’t working, use a magnet to attract the flap in the middle and it will turn red
Reply #32018-07-30
Magnetic flap level gauges need to be inspected and cleaned regularly. The float might be stuck; clean it out and it should work again. When using hydrochloric acid, be sure to take protective measures.
Reply #42018-07-30
This level gauge is a bit silly. . . The belly even rolls its eyes.
Reply #52018-07-30
The hygiene at the site is excellent; the equipment is very clean! For the white ones, just use a spare float to attract them down!
Reply #62018-07-30
In such a situation, the first thing to do is to ask the production staff whether the liquid level appears at the red mark on the upper side. If that’s the case, it can be assumed that the white mark in the middle indicates an error, and the level can be adjusted using a magnetic rod. If the actual position of the liquid level is uncertain, the best approach is to close the valve for the liquid phase of the level gauge, use a bucket to catch the liquid, open the drain valve to empty the hydrochloric acid inside the measuring tube, then close the drain valve again and reopen the valve for the liquid phase. This should normalize the liquid level. Remember to open the valve for the liquid phase slowly – you can open it a little, wait for a while, and then open it further
Reply #72018-07-30
Use a magnet to check it; the flap is out of order
Reply #82018-08-01
It’s normal for magnetic flap level gauges to have such problems; the key is to check with the control room to determine the exact level, and use a magnet to see where the float is located and whether it’s stuck.
Reply #92018-08-01
It’s normal for magnetic flap level gauges to have such problems; the key is to check with the control room to determine the exact level, and use a magnet to see where the float is located and whether it’s stuck.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.