I would like to ask everyone: for the 220V UPS circuit in the instrument cabinet of the new installation, the management requires that the neutral wire be grounded, but the design does not specify such a requirement. Is this requirement reasonable?

2018-09-05View Original

Thread Content

I would like to ask everyone: for the 220V UPS circuit in the instrument cabinet of the new installation, the management requires that the neutral wire be grounded, but the design does not specify such a requirement. Is this requirement reasonable?
Reply #22018-09-05
The HG_T20509-2014 Specification for Instrument Power Supply does not require the neutral wire to be grounded; generally, the negative terminal of a 24V supply is grounded

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.