The temperature transmitter is connected to Hart, but the device cannot be found

2018-11-03View Original

Thread Content

The E+H temperature transmitter requires a new display head; the range is to be adjusted using Hart in the calibration laboratory, but the device cannot be found. The 24V power supply is working fine – does it mean a 250-ohm resistor needs to be connected as well? Please give some guidance, thank you\ud83d\ude4f
Reply #22018-11-03
Yes, an external resistor is required; it would be easier if there were a tester available
Reply #32018-11-03
Yes, a resistor (load) needs to be added
Reply #42018-11-03
Yes, a standard resistor needs to be added, or a temperature safety gate can also be installed
Reply #52018-11-05
What kind of power supply are you using? If it’s a switching power supply, 475 volts won’t work for connection; you can use a process verifier to provide 24 volts, and then use 475 volts for the connection.
Reply #62018-11-05
Based on my personal experience, using Emerson’s own HART handheld device, it can usually be connected directly from the control room, as the host computer itself already incurs a load when performing detections; However, domestic HART handheld devices have poorer stability, and a 250Ω resistor must be connected in series. Then, connect the ends of the hand controller to the ends of the resistor, or to the ends of the instrument – either way is fine.
Reply #72018-11-05
Bro, a single-effect unit must be equipped with a resistor; even the Emerson 475, which is an imported model, requires one as well

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.