A pressure device has only one remote pressure transmitter port; if an on-site pressure display is required, can a short circuit be created at the pressure transmitter port and an on-site pressure gauge installed there? Is this in compliance with the regulations?
Reply #22018-12-08
It doesn’t meet the requirements; generally, it is required that remote transmission and pressure measurement cannot use the same pressure tapping point. But usually no one checks this. If it’s in a less important area with a low pressure level and no one will check it, then it’s okay to use it this way
Reply #32018-12-08
Can’t the display on the pressure transmitter be used as an on-site display?~
Reply #42018-12-08
The remote pressure transmitter has a display, but it cannot be used as an on-site pressure gauge
Reply #52018-12-08
Remote transmission allows display, but the text is quite small; it’s not as convenient to read as with a pressure gauge.
Reply #62018-12-08
Pressure equipment, referred to as pressure vessels, usually come equipped with flanges. Pressure transmitters are generally diaphragm-type; I’m not sure how to add this jumper. If it’s really unavoidable and adding it is necessary, I think the issue of pressure vessel inspection should be considered first
Reply #72018-12-08
If it’s connected through a pressure tapping pipe, it’s very simple: just a + tee + a manual valve will do
Reply #82018-12-08
Many of them here are installed this way.
Reply #92018-12-09
It does not meet the standards, but it’s no problem to add a tee connection; I’ve seen many such examples. It would be better if both the pressure transformer and the pressure gauge were equipped with a root valve each.
Reply #102018-12-10
Considering these three points: 1. Whether this parameter needs to be involved in interlock control; 2. Whether it is a reference value or an operating value; 3. Whether its display on-site is optional. Pressure vessels must not have holes made in them arbitrarily; if interlock control is involved, only tees can be used, and a root valve must also be installed. There are no explicit requirements in the relevant specifications regarding this aspect. If it is a non-operational quantity or a parameter that can be optional, there is no need to add fault points! (The more connection points there are, the more potential failure points there will be as well.)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.