E+H promag 50, fault code #321

2019-07-15View Original

Thread Content

This post was last edited by industrelec on 2019-7-15 at 10:07. I have a question: for an E+H Promag 50, 8-inch stainless steel sewage pipe, the error code is #321, and the actual current reading is 3.75A. My question is, do friends think it’s usually a problem with the electrodes or the circuit board? ? How to determine where the fault lies? If it’s just a problem with the board, can a Promag 53 head or board be used as a replacement? Thank you very much.
Reply #22019-07-15
Check its operation manual; the image is a screenshot of that manual
Reply #32019-07-17
The coil current is out of range; measure the coil resistance – it should be around 100 ohms generally, neither too high nor too low. If the coil resistance is fine, then check whether the plug is loose; if that doesn’t work, try using a different amplifier board
Reply #42019-07-17
After swapping the board with one from another table, the one from the other table still works fine, while this one continues to have the same issue. There is already a PROMAG 53; can it be used to replace the Promag 50 directly? ? ?
Reply #52020-06-03
Is this a problem with the sensor? I was wondering if the problem with your watch has been resolved? I now also have a watch with the same problem

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.