Requirements for the number of conductors in the instrument power cable

2021-12-01View Original

Thread Content

I would like to ask everyone: for the cable that supplies power to the instruments separately (as well as the solenoid valves), is it necessary to use a 3-core cable, or can a 2-core cable be used? Are there any regulatory requirements? 24V DC using 2x2.5mm2? 220V AC, 3x2.5mm2?
Reply #22021-12-01
24V devices usually have only two terminals for connection; even if you use a three-core cable, it won’t work. At 220V, there is usually an additional PE conductor; of course, the grounding method depends on the design of the specific system. It may not come from the power supply cabinet, but rather from a nearby grounding point, in which case it is not a three-core cable.
Reply #32021-12-01
Could you explain the design of a three-core PE grounding system? Or could you recommend any materials or standards? Thank you~
Reply #42021-12-01
Find out the differences between TN-C, TN-S, TN-C-S, TT, etc
Reply #52021-12-06
AC220V requires PE grounding protection, so it is generally three-core; DC24V can do with two cores. Article 3.1.3 of HG/T20513-2014 \"Code for Grounding Design of Instrument Systems\": Field instruments, transmitters, local switches, etc., powered by voltages below 36V do not require protective grounding unless there is a specific need for it. Article 10.2.2 of GB50093-2013 \"Code for Construction and Quality Acceptance of Automatic Instrumentation Projects\": For on-site instrument switches and similar devices with a supply voltage not exceeding 36V, protection grounding is not required unless specified otherwise in the design documents.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.