The pressure transmitter is installed outdoors in Shandong, and there is a condensation tank. How should insulation be provided in winter, and does the insulation need to be removed in summer?
I’m not sure about the average winter temperature where you are; is heat tracing available? Insulating foam and aluminum foil will suffice. In summer, it’s sufficient to turn off the heat tracing; there’s no need to remove the insulation.
It is used to measure steam at 300°C, and there is no heat tracing treatment at present.
If the pipeline is heated with steam, then the instruments should also be heated with steam; insulation foam and aluminum foil are used as well; If the pipeline does not have heat tracing, consider using electric heat tracing for the instruments, along with heat tracing cables and temperature control systems.
Heat retention is secondary; heat tracing is essential! At least water heating! Moreover, the heat tracing from the pressure tapping base to the transmitter diaphragm box must be in place! ! !
In Shandong, instruments must be insulated with heating in winter; it is sufficient to turn off the heating when temperatures drop, without the need to remove it.
I’m using ethylene glycol antifreeze; I haven’t turned on the heating system, but there is insulation in place. However, I think the insulation isn’t necessary, as ethylene glycol antifreeze has a very low freezing point, which is sufficient for normal use. It’s sufficient to prevent freezing of the pressure conduit from the condenser to the pressure measurement point – ensure it has a sufficient slope and adequate insulation
If the pressure tapping pipe is short, within 1 meter, insulation alone is sufficient; if it is very long, heating must be added
I used to live in Shandong and have experienced this situation before; insulation is necessary in such cases. You can consider using electric heating elements along with insulating material, and you can turn off the heating elements in summer