Process Engineering Section – Instrumentation and Automation Technology Forum – Daily Question – Questions 08–27: True or False? The original measurement range of the 1151GP pressure transmitter was 0–100 KPa; after a 100% zero shift, the instrument’s measurement range became: 100–200 KPa. The gauge range is 100 KPa. When a pressure of 160 KPa is applied, the gauge outputs 12 mA. Reference answer: Incorrect
Reply #22019-08-27
×, input 150kPa, output 12mA
Reply #32019-08-27
This post was last edited by Xing Jianyuan on 2019-8-27 09:56. If the current output is proportional to pressure, then the output should be (20-4)*60%+4=13.6. But I remember it seems not to be proportional; it can’t be correct, right?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.