2019-03-20View Original

Thread Content

I have a question: how can the average failure rate PFD of instruments that do not have SIL certification be estimated? Is there anything I can refer to? (The instrument has been in use for 4 years, and the manufacturer’s information is unavailable) Thank you very much!
Reply #22019-03-20
This post was last edited by Yunmu on 2019-3-26 at 12:35. Industry databases can be used for this purpose; the IEC61511-2016 standard allows the use of industry data for estimation, and such databases include E*DA, OREDA, etc.
Reply #32019-03-20
If you have enough data from your factory, you can use your own company’s data. It’s actually impossible; the sample size is too low. The data from instrument manufacturers can also be used. There is also an issue with the reliability of the data. . Unless the manufacturer also provides maintenance for your organization. In the end, the only option is to use industry databases such as e*da, ORENDA, and other similar databases.
Reply #42019-03-22
Can’t tables that have been in use for a long time be used as evidence? In that case, the SIL level will decrease over time
Reply #52019-04-13
Same question. I also have a question: Many people say that systems, instruments, etc. do not necessarily require SIL certification; it is sufficient to provide the relevant parameters so that the overall system coefficient meets the requirements of the desired SIL level. I would like to ask who determines the device parameters? Is it determined by the manufacturer, or is a SIL certification required?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.