I would like to ask about the issues mentioned by Sedo Reese

2019-12-20View Original

Thread Content

The fluctuation range is around eighty to ninety kilograms. Even after the panel on site is restarted, there are still fluctuations, but the DCS shows the value fluctuating around zero (no adjustments have been made to the process, and there are no vibration sources in the vicinity). I seek advice from experts
Reply #22020-01-06
It is recommended to check whether the probe is loose.
Reply #32020-01-08
1. Check whether the wiring cables of the instrument are loose; if they are, the instrument readings will keep fluctuating; 2. Are there any interference sources from large frequency converters in the vicinity? ; 3. Check whether the sensor is stuck; if there are any issues, please contact Engineer Li at 13924180225

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.